Cannot backup UNC station - getting an error "java.net.ConnectException".

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot backup UNC station - getting an error "java.net.ConnectException".
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1622 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot backup UNC station - getting an error "java.net.ConnectException".

Picard Product_Support
‎2018-09-06 12:52 PM

Issue

Cannot do a Save Runtime DB. - getting the following error: 
   java.net.ConnectException: Connection refused: connect 
    at java.net.PlainSocketImpl.socketConnect(Native Method)
    at java.net.PlainSocketImpl.doConnect(Unknown Source)
    at java.net.PlainSocketImpl.connectToAddress(Unknown Source)
    at java.net.PlainSocketImpl.connect(Unknown Source)
    at java.net.Socket.connect(Unknown Source)
    at java.net.Socket.connect(Unknown Source)
    at java.net.Socket.(Unknown Source)
    at java.net.Socket.(Unknown Source)
    at tridium.nre.drivers.SocketDriver$TcpSocketFactory.createSocket(SocketDriver.java:690)
    at tridium.nre.drivers.SocketDriver.create(SocketDriver.java:216)
    at tridium.nre.drivers.SocketDriver$ConnectThread.run(SocketDriver.java:510)
 

Environment

Niagara R2, UNC-520, UNC-410

Cause

The connection error typically occurs during a database backup when the port used by the UNC has been changed from the default port 80.

Resolution

If this is the case, a line must be added to the station.properties file to specify the new port value.

  1. Open the Admin Tool and log into the UNC (not the station database).
  2. Right-click on the station name that indicates "running" and select Edit > Properties.
    • The station.properties window will open (typically indicates autoStart=true and autoRestart=true).
  3. Add a line to this file that specifies the new port.
    • Example: If the station database was configured to use port 8080, the line would read ... httpPort=8080
  4. Choose File > Close and save when prompted.
  5. Reboot the UNC for change to take place
     

You should now be able to successfully backup the database. The details of this procedure are located in the documentation (Niagara Networking and Connectivity Guide).
 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6961
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore