Can the exposed dial on a STR612 be restricted, to prevent the user over adjusting the setpoint.
  • Can the exposed dial on a STR612 be restricted, to prevent the user over adjusting the setpoint.
  • sesa139513
    sesa139513
  • DavidChild
    DavidChild
‎2018-09-06 10:43 AM
User over adjusts the setpoint on the STR612
STR612
The STR612 is used in conjunction with the CZU fan coil unit controller. The user over adjusts the setpoint.
The STR612 setpoint dial can be restricted.
Under the dial cover are 2 plastic pegs that can be moved to the temperature extents that are required.