Can the I/A Series G3 kitControl Average object be configured to not output an NaN whenever any one of the inputs is NaN?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can the I/A Series G3 kitControl Average object be configured to not output an NaN whenever any one of the inputs is NaN?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1096 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can the I/A Series G3 kitControl Average object be configured to not output an NaN whenever any one of the inputs is NaN?

Picard Product_Support
‎2018-09-10 11:47 AM

Issue

Can the I/A Series G3 kitControl Average object be configured to not output an NaN whenever any one of the inputs is NaN?

Environment

I/A Series G3 (all versions)

Cause

The Average object in kitControl checks the input to see if the input is valid (Returns true if the associated value is not disabled, fault, down, stale or null.).  However, the NaN value has no affect the status of the control point.  The point status remains 'ok' causing the Average object to process the input NaN value which in turn causes the output to indicate NaN.

Resolution

The object performing the average will "drop out" the value from the calculation if the input is null versus NaN.  One workaround is to create a program object with a matching input and output of BStatusNumeric type, intercept the NaN, and replace with a null whenever the input NaN condition occurs.  The following program object contains four inputs that can be linked between the active input signals and the inputs of the Average object.

Download the nan2null (nan2Null.bog) program object and save to a known location on the computer.
Copy the nan2null program object into the station database and link as required.

Labels (1)
Labels:
  • TAC IA Series
Attachments
nan2null.zip
Tags (1)
  • Find more articles tagged with:
  • 8336
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of