Can the AS Network 8000 ASD Interface directly override a block output (DO or AO) in a MicroZone II controller on the ASD bus?
  • Can the AS Network 8000 ASD Interface directly override a block output (DO or AO) in a MicroZone II controller on the ASD bus...
  • WaynePeters
    WaynePeters
‎2018-09-06 10:31 AM
SmartStruxure, Automation Server, I/A Series Network 8000, ASD
The driver is not currently designed to perform direct override of block outputs.
There are a couple of methods to perform a block output override.
  • Directly connect to the ASD bus with XPSI and perform a System - Override to force a MicroZone II block output to a particular value for a designated period of time.
  • Add logic to the MicroZone II application to enable overrides using the devices network control EMS AI and EMS DI inputs.
  • 12926
50% helpful (1/2)