Can not import lon Lon Device template.
  • Can not import lon Lon Device template.
  • sesa150555
    sesa150555
‎2018-09-06 09:59 AM
Cannot import lon Lon Device template.
Field stays red after browsing in the correct XIF file.
Import button does still grayed out after browsing the correct XIF file.
StruxureWare Building Operation 1.3 and earlier
There is a problem with some regional settings. We have seen this using Turkish regional settings so far but the are probably other languages that will also cause the issue.
  1. Stop Workstation
  2. Open control panel
  3. Go to Regional and Language Options
  4. Change standards and formats to English. Click ok
  5. Start workstation again and import the file.
  6. Add your devices
  7. Close workstation
  8. Open Regional and Language settings and change back to your language
  9. Open workstation
Tags (3)