Can certain Analog Input values be read with up to 3 decimal places in WorkPlace Tech?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can certain Analog Input values be read with up to 3 decimal places in WorkPlace Tech?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1077 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can certain Analog Input values be read with up to 3 decimal places in WorkPlace Tech?

Picard Product_Support
‎2018-09-06 02:39 PM

Issue

Can certain Analog Input values be read with up to 3 decimal places in WorkPlace Tech?

Environment

  • WorkPlace Tech
  • MNL series
  • MNB series
  • MicroNet 2000
  • Network 8000

Cause

The MNL, MNB, MicroNet 2000 and Network 8000 controllers have the capability of working with values from -163.83 to 16,383 and never use more than 2 digits after the decimal place. This is something that all of the controllers have used for many years. This is documented on page 25 of WorkPlace Tech Tool 4.0 Engineering Guide (F-27254).

Resolution

In certain applications where it is necessary to read very small values beyond 2 decimals, a work around has been used.  The technique should only be used by those who fully understand the concept and its implementation.  The technique to overcome this is to set the output scaling factors of the Analog Input object (in WorkPlace Tech) to values at a factor of 10 or 100 (or other suitable number) thus giving the resolution and therefore (no loss of) accuracy that is required.  This requires scaling the value down by the same factor at the head-end (or wherever) to get the proper and accurate reading.  Multiply the scale properties by a factor then divide by the same factor for display or logic calculations.

Example:  A pressure transmitter that reads a pressure range of -.25 to .25 in. wc at 4 to 20 mA, the Analog Input properties needed for such a transmitter would be as in this table:

Input Low Value:     4 mA
Scaled Low Value:  -.25 inwc
Input high Value:     20 mA
Scaled High Value: .25 inwc

There is an issue with a device that has such small sampled values.  The controllers can only register at most 2 digits after the decimal.  Therefore the controller can be fooled by setting the properties such that the controller thinks that it has a device transmitter attached that reads pressures from -25 to 25 In. WC.  This is a factor of 100 and all values would be 100 times larger than the true reading.  This of course needs to be accounted for in any calculations and GUIs.  The properties for this would be as in this table.

Input Low Value:      4 mA
Scaled Low Value:  -25 inwc
Input high Value:     20 mA
Scaled High Value: 25 inwc

In using this technique, remember to factor the number when displaying it or using it with other logic.  Since the controller can use negative numbers no smaller than -163.83, no properties can be entered smaller than that value.  In the table below the same transmitter is used but a factor of 1000 is used for the properties.  This can not work due to the scaled low value being less than -163.83.

Input Low Value:     4mA
Scaled Low Value: -250 inwc
Input high Value:     20 mA
Scaled High Value: 250 inwc

The workaround is well proven and sufficient to satisfy needs.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3386
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of