Can a deadband be controller in a Loop Object in Continuum
  • Can a deadband be controller in a Loop Object in Continuum
  • ScottLeedberg
    ScottLeedberg
‎2018-09-06 02:06 PM
Trying to control the deadband of a Loop object
CyberStation
BCX
I2
B3
There is no deadband attribute of a Loop object in Continuum
What is exposed are the PID parameters:
Controlled Variable
Controlled Variable units
COV Increment
Proportional Value and Units
Integral Value and Units
Derivative Value and Units
Bias
Action
Having the system in control for each mode is efficient unless the building itself is not very energy efficient. If that is the case, then I would limit any optimal start times to no more than 2 or 3 hours. If no optimal start/stop is being used, then just enabling and disabling the loops within his +/- 3 deg window should be sufficient.
  • 4682
This is a heading