Can a Script Function be used in the Conversion line of a BACnet b3 controllers analog input?
  • Can a Script Function be used in the Conversion line of a BACnet b3 controllers analog input?
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
‎2018-09-06 09:17 AM
If the conversion line on an input is more complex than a single line of script, can a function be used?
BACnet b3 Controller Analog input conversions / scaling.
Script programming, functions
The code required to scale an input is more complex than a single line of code.
It is not possible to use a Script Function in the conversion line of an input point, however quite complex formulas can still be entered that scale the ElecValue when the point is evaluated.
The format of an input point conversion line is still:
    ElecValue / 1000
The automatic scaling table is also available in the b3 inputs for linear conversions
Tags (2)
  • 17021
  • analogue