Can a LA-1 L-Bus adapter be used on the Netcontroller II?
  • Can a LA-1 L-Bus adapter be used on the Netcontroller II?
  • sesa116834_brid
    sesa116834_brid
‎2018-09-06 02:43 PM
Netcontroller II (9680)
In order to communication on a port other than Comm 4, an LA-1 must be added.
The Netcontroller II (9680) comes with direct L-Bus option already on Comm4 without having to use the LA-1 adapter. However if you would like a different port to support L-Bus instead of Comm 4 the LA-1 can be added to Comm 1.
Note: When using L-Bus you will not be able to connect IOU modules.