Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Can LONMark Devices be used with Continuum?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can LONMark Devices be used with Continuum?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1590 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can LONMark Devices be used with Continuum?

Picard Product_Support
‎2018-09-10 03:59 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:34 AM

Issue

If it is possible, what is the best way to integrate LONMark devices to Continuum?

Product Line

Andover Continuum

Environment

  • Continuum Netcontroller CX9900, CX9940, Netcontroller II CX9680
  • Echelon LON X Driver, XDriver, X-Driver
  • LONMark, SNVTs, Bridge, Gateway

Cause

Clarification required on LON compatibility.

Resolution

FTT Versions of both the Netcontroller and Netcontroller II can be configured to communicate with 3rd party LONMark devices. You need to use the 1st generation or 2nd generation X Driver file respectively for these controllers.

The FTT-10 port Comm16 has to be selected to be in LONMark X Driver mode, this is done in the Web page or the HyperTerminal Window connection.

Once in LONMark mode you can not connect any IO Modules to the controller.

The LONMark X Driver allows data to be mapped between the Continuum system and a LONMark Network. You create X Driver points in the Netcontroller II defining the SNVTs they will be seen as in the LON system.
You then will need to design a LON Network that will consist of the NCII LON port (Comm16) and the other LON Devices to be connected. This network will need to be designed using the correct LON cabling and terminations. You will need a PC with appropriate NIC card to run the Lonmaker 3.2 software or the NL220 software to design your LON network and create all of the bindings between the different devices. The LON X Driver will act as a bridge between the LON and the Continuum networks.

Both Lonmaker 3.2 and NL220 can be ordered through Schneider Electric along with any LON routing devices that may be required in the LON network design, these parts will be in the Vista product catalogues and price lists.

Details of the configuration of the X Driver points are detailed in the LONMark X Driver User Guide.

The Latest Echelon LonMark X Driver software for the FTT Netcontrollers can be downloaded from The Exchange Download Center.

Note: Unlike other X Drivers, the LONMark driver does not require a port to be X Driver enabled to operate.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5185
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore