Can I edit the "covIncrement" of a BACnet point in a BACnet controller from the ENC?
  • Can I edit the "covIncrement" of a BACnet point in a BACnet controller from the ENC?
  • Kim_Baze
    Kim_Baze
‎2018-09-06 10:04 AM
G3 ENC's
This may be necessary to increase the covIncrement of a BACnet point if it is triggering excessive "cov notifications" to the ENC.
In revision 3.2 and newer under the Device object a new selection called “Virtual” was added. BACnet virtual points are transient and are created and subscribed only when accessed. Expand Virtual and all the BACnet objects in the device are listed. Right click the object of interest and all of its properties are displayed, including covIncrement. Expand covIncrement and its value can be changed. When the Save is done the value is written to the controller.
  • TAC IA Series
  • 14361