Can I add BACnet MSTP to an I/A Series R2 or G3 JACE-NXT hardware platform?
  • Can I add BACnet MSTP to an I/A Series R2 or G3 JACE-NXT hardware platform?
  • WaynePeters
    WaynePeters
‎2018-09-06 12:38 PM
I/A Series R2, G3, JACE-NXT
The JACE-NXT platform is based on a Microsoft Windows software platform (Windows XP) that is unable to support the token passing required for BACnet MSTP.
Options are ...
1. Use another device that can act as a router between BACnet MSTP and BACnet IP or BACnet Ethernet (e.g. MNB-1000, etc.).
2. Use a different R2 or G3 hardware platform that provides direct connection to the BACnet MSTP device (e.g. UNC-520, ENC-520, etc.).
  • TAC IA Series