Cameras can't be learned in Continuum except one
  • Cameras can't be learned in Continuum except one
  • YangboLIU
    YangboLIU
‎2018-09-06 10:50 AM
When integrate with Pelco Endura system, after configure video serer in continuum correctly, there is only one camera can be found, the other cameras not come in.
Continuum 1.92~1.94
Endura 2.0
The cameras in Endura not be assigned a sequence number.
  1. Ask Endura engineer to set a unique number to each camera
  2. Click "learn Camera" in Continuum video server editor
After the above steps done, all the cameras will come in Continuum if the connection in Endura side is correct.
Tags (6)
  • 11967
  • camera
  • endura
  • learn
  • server
  • video