Calibrate temperature sensors on a Xenta programmable controller.
  • Calibrate temperature sensors on a Xenta programmable controller.
  • SESA116857
    SESA116857
‎2018-09-10 03:24 AM
How can a temperature input be calibrated in a Xenta programmable controller.
Menta 5.x.x
The sensor input block in Menta does not have any calibration features. Instead these must be done with the program by the use of a calibration value.
Use a PVR block and add this value to the raw senor input value to result in a calibrated value.
By making the addition block public and giving it a name it will be visible from a Vista front end. If necessary it can be output as a SNVT as well.
In this situation it might be advised to leave the AI block SAT_Raw public flag unchecked to provide a less cluttered view to the end user. While the calibration PVR is left at zero you will see the raw value from the sensor.
  • 6375