Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

CZT, CXT, CXR, DC1100, DC1400 Controllers PID Control

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • CZT, CXT, CXR, DC1100, DC1400 Controllers PID Control
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8216 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

CZT, CXT, CXR, DC1100, DC1400 Controllers PID Control

Product_Support
‎2018-09-10 03:44 AM

Last Updated: ContentModerator Explorer ‎2025-08-11 04:06 AM

Issue

What are CZT, CXT, CXR Controllers?

Why are CZT, CXT, CXR Controllers used?

What is Proportional, Integral Action and Derivative control.

Why does a controller deliver different pulse lengths to the valve and not drive it fully open or closed?

What is Pb, IA, PID?

Environment

  • CZT
  • CXT
  • CXR
  • DC1100
  • DC1400
  • Proportional, Integral Action, Derivative, Pb, IA, PID

Cause

What do these controllers do and what are their applications?

What is Proportional, Integral Action and Derivative control.

Why does a controller deliver different pulse lengths to the valve and not drive it fully open or closed?

What is Pb, IA, PID?

Why is a 0-10V Signal used?

Why is a 3 point control / Open Closed actuator used?

Resolution

Proportional Controllers are used in applications where there are long time lags e.g. room control, return air control, storage calorifier (HWS). Where the controlling sensor is a medium to long distance from the heat/cooling source.

An example of a proportional controller is the Satchwell CZT.

Integral action controllers are used in applications where there are short time lags e.g. supply air control, frost coil control, non-storage calorifiers. Where the controlling sensor is a short distance from the heat/cooling source.

An example of a integral controller is the Satchwell CXT or the CXR. The CXR is a controller where the supply air is controlled, but the setpoint is reset by the return air or space temperature, therefore the time lag is short. Other controllers that fall into this category are the DC1100, DC1400 again the controlling sensor (mixed flow temp) is located a short distance from the heat source. 

The term proportional band (Pb) is where the valve is moved to a position proportional to the deviation from setpoint. 0-10V modulating actuators are generally used on these controllers.

The term integral action (Ia) is where the valve is moved at a rate according to the deviation from setpoint i.e. the valve is given longer pulses the further away from setpoint, shorter pulses as it gets closer. 3 point control/pulsed pair/open-close actuators are generally used on these controllers.

Further to proportional controllers, inherent offset (the setpoint is never quite reached) can be an issue. Integral action can be applied to remove this offset. These controllers are primarily proportional, but integral action can be found on them and is applied. Hence the term PI or PI controller.

Derivative control is generally only found on BMS controllers and is used occasionally with PI control, hence the term PID. Here the derivative action moves the valve proportionally to the change from setpoint. It is complex and is rarely used.

Further detail about CSC controllers can be found here.

Further detail about CXT controllers can be found here.

Further detail about CXR controllers can be found here.

Further detail about CZT controllers can be found here.

Further detail about DC1100 and DC1400 controllers can be found here.

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6479
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore