Issue
CSC5252 and CSC5352 Climatronic Compensator Controller will not display Room Temperature.
Environment
Satchwell
CSC5252
CSC5352
Climatronic
Compensator
Controller
Room
Temperature.
Cause
CSC5252 and CSC5352 Climatronic Compensator Controller may not display Room Temperature for the following reasons :-
1. No Room Temperature Sensor installed.
2. Room Temperature Sensor installed but ROOM INFLUENCE MODE default value in CSC Controller has not been amended..
.
Resolution
CSC5252 and CSC5352 Climatronic Compensator Controller may be set to display Room Temperature as follows:-
1. Ensure Room Temperature Sensor is installed and connected to CSC Controller Room Temperature Sensor Input terminals.
2. Ensure ROOM INFLUENCE MODE (INF) setting in CSC Controller Fine Tune Mode is set to value = 1
N.B.
Sensor connection details and the means of entering and exiting the CSC Controller Fine Tune Mode both appear in the Climatronic CSC5352 and CSC5252 Compensator User Guide, a copy of which may be viewed here.