Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

COV Increment and how it can affect the Bacnet traffic on a network

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • COV Increment and how it can affect the Bacnet traffic on a network
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
9711 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

COV Increment and how it can affect the Bacnet traffic on a network

Picard Product_Support
‎2018-09-06 03:33 PM

Issue

COVNotification messages in BACnet captures.

Product Line

EcoStruxure Building Operation

Environment

  • BACnet IP network
  • BACnet MSTP network
  • BACnet networks with controllers that support COV (Change of Value)

Cause

COV increment is an attribute that is available in several BACnet points that is settable and when this attribute COV Increment is left at a setting of zero can cause COVNotification messages appearing as broadcast storms creating un-necessary network traffic.

Resolution

It is suggested to set the value of the COV increment attribute to something other than the default zero or to a value that is pertinent to the point in question. The COVNotification services are uni-cast messages and can have a many to one relationship depending on how may clients are subscribing to the point.

Example:

Jobsite has a BACnet OAT (outside air temp) input point with the COV increment of zero. The OAT point is added to the watch window or a binding to a graphic or program. The OAT is changing ridiculously fast due to wind and intermittent clouds. The value is changing by 1/1000 of a degree and each COV (change of value) message is delivered out to any object that is referencing the point. But does the value need to display or do we care if the point changes by 1/1000 of a degree. Let's say that the sites requirement only needs value changes of 2 degrees or more. The COV increment can be set to 2.0 and now the UnconfirmedCOVnotification message would only be sent if the OAT changed by 2 degrees or greater. This alone would reduce 100's if not 1000's of network packets. Imagine a jobsite with the above scenario and 100 different points all with the COV increment of zero.

Setting the COV increment to something other than the default of zero is one of many ways to improve BACnet communications and reduce what may appear as broadcast storms on the network.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 7530
Was this article helpful? Yes No
100% helpful (8/8)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.