Building Operation EWS Hardware folder blank using Security Expert Smart Connector

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Operation EWS Hardware folder blank using Security Expert Smart Connector
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
427 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Building Operation EWS Hardware folder blank using Security Expert Smart Connector

Picard RobertAndriolo Picard
‎2025-09-22 06:02 PM

on ‎2025-09-22 06:02 PM

Issue

After installing or upgrading the Security Expert SOAP Service to 1.7.0 (or above), the Building Operation EcoStruxure Web Services (EWS) Hardware folder (container) under SecurityExpert

  • appears blank, preventing users from viewing or
  • Not possible to Host EWS Objects
  • Objects in Building Operation no longer update

Product Line

EcoStruxure Security Expert

Environment

  • Building Operation Enterprise Server
  • EcoStruxure Web Services
  • Security Expert
  • SOAP Service: Version 1.7.0.0 or greater
  • Smart Connector Framework Version 2.5.5.108
  • Security Expert Smart Connector Extension: Version 1.2.0.22

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed correctly. Before beginning these steps, make sure all essential data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

This issue typically occurs when:

  • Incompatible versions of SOAP, Smart Connector, or Security Expert are installed.
  • The latest (or higher) Security Expert Smart Connector Extension (v1.2.0.22) is not used.
  • The installation guide referenced is outdated and does not reflect the latest version requirements.

Resolution

To resolve the issue, follow these steps:

  1. If upgrading Security Expert, it is recommended to Uninstall any existing versions of:
    • EcoStruxure Security Expert
    • SOAP Service
    • SmartConnector Framework
    • Security Expert Smart Connector Extension
  2. Install the following versions as per the Instructions provided in Step 3:
    • SOAP Interface: 1.7.0.0 or greater
    • SmartConnector Framework: 2.5.5.108
    • EcoStruxure Security Expert: 4.3.370.1 or greater
    • Security Expert Smart Connector Extension: 1.2.0.22
  3. Follow the instructions in the updated installation manual:
    • schneider-isc.uk/file/ 
      • Search for Document name Security Expert SmartConnector Version 1.2.0.22 - Installation & User Manual
    • Download Extension v1.2.0.22 → Using this link schneider-isc.uk/file_download/, navigate to
      • Smart Connectors
      • Security Expert Smart Connector Extension
      • V1.2.0.22.zip

Additional Notes

  • The current Security Expert - Smart Connector Extension - Installation Guide on the EcoXpert site does not yet include version 1.2.0.22. An update is pending. Please use the link above.
  • Always verify that all components are aligned with the supported versions listed above.

 

.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore