Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Bug in conversion of real numbers to integers in Menta Expression Blocks

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Bug in conversion of real numbers to integers in Menta Expression Blocks
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1242 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Bug in conversion of real numbers to integers in Menta Expression Blocks

Picard Product_Support
‎2018-09-06 02:28 PM

Issue

Bug in conversion of real numbers to integers in Menta Expression Blocks

Environment

TAC Xenta 280/300/401 with system program version up to version 3.41

Cause

A bug exists that causes real numbers to be improperly converted to integers in Expression Blocks. The issue is that some functions that return a real result (e.g. +-*/ and exponentiation) will sometimes return a value slightly less than expected.

For example, 2**5, which is 2 to the fifth power, should return 32. Instead, 31.9999999999 is returned. In an expression that then then converts this to an integer (e.g. "A&(2**5)"), the result gets truncated to 31 instead of the expected 32. In the example "A&(2**5)", A will then be bitwise AND-ed with binary 01111 instead of 10000.

Unfortunately, this bug is only seen when running the code live on a controller. In offline simulation mode, 2**5 returns the correct value of 32, which only makes the bug more difficult to diagnose. Oddly, The XPI block and the INT() function convert results to integers differently. An XPI block with expression "2**5" will return 32. However, and XPI block with expression "INT(2**5)" will return 31. In some cases (e.g. 19**3) both the XPI block and the INT() function return the incorrectly truncated value.

This behavior is corrected from version 3.50 of TAC Xenta 280/300/401

Resolution

The work-around is to never use operations that return real values in an expression that also does operations that convert the operands to integers (such as bitwise operations).

This behavior is corrected from version 3.50 of TAC Xenta 280/300/401

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3909
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of