Bound values pushed to BACnet device stop updating after power is cycled to the device.
  • Bound values pushed to BACnet device stop updating after power is cycled to the device.
  • AbeMeran
    AbeMeran
‎2018-09-06 09:06 AM
Have some values being pushed to a BACnet Loytec L-VIS device via mirrored point in the AS, after the L-VIS screen is powered down/up the bound values are pushed on the next change, for analog value this does not present a big problem as they change frequently, but for binary values is a problem.
BACnet
AS
Guaranteed transfer has not been configured on the binding.
Set a transfer interval in 'Guaranteed transfer even if value has not changed'
In the example below, the value will be pushed out once a minute regardless of whether it has changed or not.
  • 17860
100% helpful (1/1)