Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Bit switch settings on the MicroNet Mi when connected to a Xenta, VisiSat, or SBO Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Bit switch settings on the MicroNet Mi when connected to a Xenta, VisiSat, or SBO Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Gary
    Gary

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3717 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Bit switch settings on the MicroNet Mi when connected to a Xenta, VisiSat, or SBO Server

Picard Product_Support
‎2018-09-07 08:15 AM

Issue

Failing communications when Xenta 555/731, VisiSat, StruxureWare Building Operations automation server/enterprise server connected to MicroNet ARCnet system through an MNMi.

Product Line

Satchwell MicroNet, TAC Vista, EcoStruxure Building Operation

Environment

  • Xenta 555 or Xenta 731 communicating to a MicroNet ARCnet LAN
  • VisiSat communicating to a MicroNet ARCnet LAN
  • StruxureWare Building Operations automation server/enterprise server communicating to a MicroNet ARCnet LAN

Cause

MicroNet Mi bit switches not set correctly.

Resolution

Cold Starting a MicroNet Mi

Caution: The cold start procedure clears all configuration data from the non-volatile EEPROM of the device and reloads default settings. A cold start is performed using bit switch S1, as shown in the following diagram.

To perform a cold start:

  1. Energise the device and verify that the RUN LED flashes at about once per second.
  2. Unplug any connections to 9 pin plug 3 and 9 pin plug 4.
  3. Set all switches to the off position.
  4. Place bit switch 8 in ON position and then return to OFF position. You will not see anything change.
  5. Place only switch 1 in the ON position. The remaining switches must be in the OFF position.
  6. Place bit switch 8 in ON position and then return to OFF position. You should see the RUN, WINK and MODEM LEDs remain lit for about 1.5 seconds, then the RUN LED should flash at about once per second.
  7. Switch 1 only must be ON for direct connection to Xenta 555.

Note: This is different from the cold-start procedure for a controller, which requires you simply to toggle switch 8. See data sheet DS10217A for more information.

Labels (3)
Labels:
  • EcoStruxure Building Operation
  • Satchwell MicroNet
  • TAC Vista
Attachments
Tags (3)
  • Find more articles tagged with:
  • 4830
  • bitswitch
  • dipswitch
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore