BioScrypt V-Pass-2 (Biometric) Reader in I/NET Seven

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BioScrypt V-Pass-2 (Biometric) Reader in I/NET Seven
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Tom_Poovey
    Tom_Poovey

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2828 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BioScrypt V-Pass-2 (Biometric) Reader in I/NET Seven

Picard Product_Support
‎2018-09-07 02:32 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-26 12:47 PM

Issue

How to program a BioScrypt V-Pass-2 (Biometric) Reader in I/NET Seven.

Product Line

Other, TAC INET

Environment

I/NET Seven

BioScrypt V-PASS (MV1200)

Cause

Assistance with configuring the BioScrypt V-PASS reader with I/NET Seven Access Control.

Resolution

Biometric Reader Setup

Using the Bioscrypt V-pass-2 Reader

The reader is:
Bioscrypt V-Pass FingerPrint Reader VPASS-2
Note: The Programming software to load fingerprints on the PC comes with the reader.

For the actual wiring and programming of this reader see the linked "BioScryptSetup.PDF" BioScript Setup

Wiring (pigtail)

Wiegand

1 - Wiegand Out Data 0
3 - Wiegand Out Data 1
6 - Wiegand GND

Power using separate 24V DC Power Supply

11 - Pwr GND
13 - Pwr IN
15 - Earth Ground

BioScrypt V-Pass Reader Wiegand Setup

Install BioScrypt Software (VeriAdmin) on PC and setup to communicate with reader.

  1. Go to Configure > Unit Parameters
  2. Click on Wiegand Tab
  3. Check Predefined Format
  4. Pick "Standard 26 bit"
  5. Under On Success
  6. Check Alt Site Code & Enter Arbitrary Value (usually 3 digits)
  7. RECORD VALUE this is the Site Code
  8. Under Wiegand I/O
  9. Check Enable Input
  10. Check Enable Output
  11. Select Always Output (regardless of Input Source)
  12. Enroll Individual in VeriAdmin

Enroll Individual
RECORD ID – this is Individual Number

NOTES: The index number is to assigned to ID number to record each individual finger (0-9 is for all 10 fingerprints). I/NET will only be sent the ID number in the Wiegand String.

Schedule does not matter. You have selected Always Output (regardless of Input Source). One will do all the door scheduling in I/NET.

Enroll Individual in I/NET

Create new Tenant called “BioReaders”

If site is using Wiegand Card and NOT Large Numbers (Dipswitch 7 OFF)
Enter Site Code (recorded from above) as the Tenant ID
When enrolling the individual in the new tenant, use the ID recorded from above as the Individual Number and Decimal Card Number.
 
If site is using Wiegand Cards and Large Numbers (Dipswitch 7 ON) or if using Idiscs (set Dipswitch 7 ON for only DPUs with BioScrypt, even if they have Idisc also)
Leave default Tenant Code.
Use 26BHEXCAL.xls and enter Site Code and Individual ID recorded from above and it will generate the HEX Card Number.
When enrolling the individual, enter the Hex Card Number as generated.

I/NET Door Configuration

Make sure door is setup as Wiegand 26

Configuration as Implemented

DPU 7920
Door 08 was setup as BioScrypt V-Pass MV1200
Door 09 was setup for Idisc

Door Lock was wired to both relays in series (so both had to be energized to unlock the door).

Door 08 (BioScrypt) was given a schedule of 24/7 and assigned to all individuals in new tenant.
Door 09 (Idisc) had the original schedule assigned to site personnel.
This schedule is the one that will deny access according to schedule.

Other Configurations

This can be used as a single reader for the door (with schedules in I/NET) or as implemented above with any combination of reader compatible with I/NET.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (1)
  • Find more articles tagged with:
  • 2887
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore