Binding Templates and Device Templates imported into the ES are not automatically distributed globally into the Automation Servers below the ES
  • Binding Templates and Device Templates imported into the ES are not automatically distributed globally into the Automation Se...
  • SESA128463
    SESA128463
‎2018-09-06 10:37 AM
After a template has been loaded in the ES, you will not see this template listed in the list of templates on any of the AS devices that reside under that ES.
  • Binding Templates
  • Device Templates
  • xif files
  • DRF Kits
  • Enterprise Server
  • Automation Server
SmartStruxure designates separate levels between the AS and ES to prevent unnecessary distribution templates that will use up the memory in the AS.  For example, it is possible to have Binding Templates that have a great use in the ES but little to no use in the AS.  For this reason, you will need to take an extra step to load the necessary templates into the AS if needed.
NOTE:  There is not currently a function to delete unwanted templates out of a device in SmartStruxure.  Make sure the correct template is selected before you complete the import process.
You will be required to import that all of the necessary templates into the ES and all of the AS devices that may require a use for that particular template. This can be done by simply logging directly into the AS to load the template locally.