Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Belkin Bluetooth adapter (F8T01n) on WIN 7 32-bit computer won't connect to MNB-ROAM-IA.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Belkin Bluetooth adapter (F8T01n) on WIN 7 32-bit computer won't connect to MNB-ROAM-IA.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3190 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Belkin Bluetooth adapter (F8T01n) on WIN 7 32-bit computer won't connect to MNB-ROAM-IA.

Picard Product_Support
‎2018-09-06 11:33 AM

Issue

Belkin Bluetooth adapter (F8T01n) on WIN 7 32-bit computer won't connect to MNB-ROAM-IA.

Environment

PC with Windows 7, 32-bit operating system
Belkin Bluetooth adapter, model # F8T016 - F8T017
MNB-ROAM-IA
WorkPlace Tech 5.x, configured for BACnet/ MSTP communications with MNB-ROAM-IA

Cause

The instructions for installing the Belkin Bluetooth adapter as documented in F-27578, TAC I/A Series ROAM-IA Quick Start Guide, "Windows XP-Specific Instructions for Bluetooth Installation", do not apply to installing the adapter on a computer with the Windows 7 operating system. 

The procedure is substantially  different in "look and feel" on a Windows 7 computer than on a Windows XP machine - the instructions for Windows XP are not much help on a Windows 7 installation.

Resolution

The following series of screen captures will illustrate the procedure for installing a Belkin Bluetooth adapter on a Windows 7, 32-bit machine.

1. According to the Belkin FAQ shown, "Most Belkin Bluetooth USB adaptors install automatically without any extra software on Windows 7. Simply plug the device into a spare USB Slot. Windows 7 should automatically recognize the device and install the necessary drivers and software."  This was the case on the laptop PC tested, a Dell Latitude E5500.

Screen prompts indicated that the drivers were loaded successfully, and the device was ready to use.

2. Open the Device manager, and there will be a folder for Bluetooth Radios. Expand the node, see the Generic Bluetooth Adapter.

3. Switch on the MNB-ROAM-IA.

A Bluetooth icon will be added to the Windows Toolbar.

4. Click on the icon to bring up a menu. From the menu, select "Add a Device". The wizard will search for Bluetooth devices within range, should find the tac-RoamIA:nnnnnnn, where nnnnnnn is the serial number of the MNB-ROAM-IA. This should match the label on the back of the MNB-ROAM-IA

5. Pressing the "Next " button will bring up the "Select Pairing Option" screen.

6. Select the middle option, "Enter the device's pairing code", and press "Next". This brings up the following screen.  Type the pairing code "tac" in the box. The code is case-sensitive, must use lower-case as shown.

7. When the MNB-ROAM-IA has been successfully added and paired, the wizard will display the status.

8. Click on the hyperlink for Devices and Printers to verify that the device has finished installing properly, as follows.

9. In the Windows Device Manager, a Bluetooth Radios folder should be displayed. Expand the folder to see the Generic Bluetooth Adapter.

10. Right-click on the Generic Bluetooth Adapter, go to its Properties, Driver tab. The driver shown (6.1.7600.16385) was installed when the adapter was first plugged into the USB port

 

11. In the Device Manager, expand the ports folder, and two "Standard Serial over Bluetooth link" ports are shown, COM15 and COM5

12. Use the port with the lower number in the WorkPlace Tech communications setup for the MNB-ROAM-IA. In the example shown, COM5 is selected. Press the "Test and Configure Connection" button.

13. When communications are successfully established, the blue LED on the MNB-ROAM-IA will be ON continuously.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 11098
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore