Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Battery life in Andover Continuum controllers that have onboard batteries.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Battery life in Andover Continuum controllers that have onboard batteries.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • PaulFr
    PaulFr
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3361 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Battery life in Andover Continuum controllers that have onboard batteries.

Picard Product_Support
‎2018-09-06 02:12 PM

Issue

Is there a way to tell if the battery is bad in a controller?

Product Line

Andover Continuum

Environment

  • BCX - 4000, 4040, 9640
  • ACX5740, 5720
  • Netcontroller II 9680
  • Infinet II controllers
  • B3 controllers

Cause

Determine if a battery is good

Resolution

Battery health is tricky to measure.  Open circuit voltage COULD look ok with a marginal battery.  The only sure way is to pull the power on the Netcontroller and see if it holds the data for our specified time.  Most sites will not want to take their controller down for that long. Take the battery out and measure it with a voltmeter, it should read not much lower than ---

  • BCX and ACX model controllers  3.6V
  • Netcontroller II, Infinet II and B3 controllers 2.7V

BCX Spec Battery section:

Replaceable, rechargeable battery. Provides 30 days typical accumulated power failure backup of RAM memory All data stored in Flash on power loss.

ACX Spec Battery section:

Replaceable, rechargeable battery. Provides 7 days typical accumulated power failure backup of RAM memory All data stored in Flash on power loss.

I2/B3 Coin type battery:

The small coin battery in the i2 / b3 is rated 41mAH;  if you calculate based only on the SRAM and RTC current draw you get about 85 days. 

Netcontroller II:

The battery type here and SRAM are typical of infinet II controller battery life and will maintain backup of SRAM down to 2.7v.

NOTE:

Backup Flash is non-volatile memory and once written will hold unless manually cleared. SRAM is a part of memory that holds information as to where to start programs when power is re-applied to the controller in cases of main power loss.

The problem is that battery life is highly dependant on number of charge / recharge cycles which is beyond our control.   You don't find the battery manufacturers giving such specs either.  Example:  The coin cells in our i2 / b3 have a shelf life "up to 10 years". Day to day use it is suggested that batteries should be replaced every 5 years.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4482
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore