Backwards Compatibility between Enterprise Servers and SmartX Servers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Backwards Compatibility between Enterprise Servers and SmartX Servers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2364 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Backwards Compatibility between Enterprise Servers and SmartX Servers

Admiral David_Kendrick Admiral
‎2020-02-05 03:35 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:34 AM

Issue

There is potential for confusion around the backward compatibility offered in EcoStruxure when the version of Enterprise Server differs from that of Automation Servers in the same system

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation SmartX Servers

Cause

The 3.1.1 Release Notes refer to a new 'Multi-version system' with the possibility of a v3.1 Enterprise Server but with v3.0 Automation Servers able to function long term within the same system (albeit with some engineering limitations).   

This implies that AS running earlier versions than v3.0 cannot coexist, attempts to add AS running v2.0 to ES running v3.0 have produced errors.

However........
The System Upgrade Reference Guide refers to 'Runtime Compatibility' with Version 3.1 that states that Automation Servers running v1.8, 1.9, 2.0 and 3.0 can all coexist with an ES running 3.1 without issue

Resolution

Both documents are true, but there are two possible situations that need to be considered:

Situation 1)
A site has a v1.9 or v2.0 system which is required to be upgraded to v3.1.
When upgrading, the ES is usually the first device to be upgraded, then depending on the number of AS onsite it may take a period of time to upgrade all the AS (especially if some of these servers are used in hospital theaters etc).
For this reason EBO has an Upgrade Runtime Compatibility from v3.1 back to to v1.8, 1.9, 2.0 and 3.0, which means that an AS already in the system when the ES is upgraded to 3.1 will maintain connectivity and functionality while the upgrade takes place.

Situation 2)
A site has an external v1.9 or v2.0 AS whichis required to be added to an ES which is already running at v3.1.
When trying to add in a new controller to a v3.1 ES, an error is produced stating that the version of the AS being added needs to be updated to before it can be added.

Error Message when adding v2.0 AS to v3.0 ES
3.0.x message.png

Error message when adding 2.0 AS to 3.1 ES (better explanation)
3.1.x message.png

To summarize EBO does have Runtime Compatibility from v3.1 back to 1.8 as stated, but only for AS already in the system at the time of upgrade.

Once upgraded to v3.1 the multi-version environment can be used to operate AS at v3.0 but adding AS running versions before 3.0 will generate a descriptive error.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidKendrick20
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore