Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Backing up a GCM database in Tree Tech, but the system wasn't originally engineered using Tree Tech.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Backing up a GCM database in Tree Tech, but the system wasn't originally engineered using Tree Tech.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1445 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Backing up a GCM database in Tree Tech, but the system wasn't originally engineered using Tree Tech.

Picard Product_Support
‎2018-09-07 05:06 AM

Issue

Backing up a GCM database in Tree Tech, but the system wasn't originally engineered using Tree Tech. Is there a documented procedure for doing so?

Environment

Tree Tech 3.1 or 3.2

Tree Tech Engineering Guide, F-26640-4

Network 8000 GCM-84000, GCM-86000, LNC-1000, SIM-x

Cause

Earlier versions of the Tree Tech Engineering Guide, F-26640, didn't include a step-by-step procedure for backing up a GCM that had not originally been engineered using Tree Tech.

Resolution

The latest edition, Tree Tech Engineering Guide, F-26640-4,  has been appended to include a step-by-step procedure for creating and configuring all Tree Tech components necessary for ultimately uploading a GCM database. A link to this revised edition is available through the "Help" menu:

 

 

See Appendix B, "Creating a GCM Database Backup".

Topics include:

1. Creating a New Project Database

2. Adding the Equipment Segment

3. Adding the Network 8000 Object

4. Adding a GCM to the Network

5. Adding the Workstation Segment

6. Adding a Port

7. Configuring the NETWORK 8000 Network

8. Communicating with the GCM

9. Prepare for Backup (Upload)

10. Uploading the GCM Database

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 13704
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore