Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet performance issue after installing or upgrading to 1.7.1 and later

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet performance issue after installing or upgrading to 1.7.1 and later
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Dave_Shore
    Dave_Shore
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1709 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet performance issue after installing or upgrading to 1.7.1 and later

Picard Product_Support
‎2018-09-10 02:19 PM

Issue

After upgrading to version 1.7.1 or later, a performance issue is seen when reading BACnet values from BACnet/IP devices.

The CPU usage on an Automation Server is continuously high.

Product Line

EcoStruxure Building Operation

Environment

  • Detected in version 1.7.1
  • Automation Server
  • Enterprise Server
  • BACnet/IP

Cause

A new "BACnet ReadPropertyMultiple Service" has been included from version 1.7.1. Data retrieval from devices that support ReadPropertyMultiple service and do not support the COV (Change of Value) service has been optimized. The resulting improved polling behaviour will particularly benefit graphics performance for ReadPropertyMultiple.

If a site is upgraded to version 1.7.1 where this improved communication service gets used automatically, it is possible that the server CPU usage increases. This issue will only be seen if the third party device does not support COV subscriptions, does support ReadPropertyMultiple and a large number of values are being requested from the same device e.g. using bindings. This is a result of much more data being requested by the Server in the same time period. 

From Release Notes version 1.7.1
3.4.4 Improved polling performance

Data retrieval from devices that support ReadPropertyMultiple service and do not support the COV (Change of Value) service has been optimized. The resulting improved polling behavior will particularly benefit graphics performance for ReadPropertyMultiple.”

Resolution

  1. Select the BACnet interface where the performance issue is seen
  2. Select the advanced properties for the interface
  3. Change the “Minimum polling interval for local IP networks (ms) to “3000”
  4. In case the BACnet interface is configured in an Automation Server, test other values in step 3 until the CPU usage is stabilized

You can check the AS CPU usage, by dragging the CPU usage property to the watch window in WorkStation

NOTE
It is also worth setting the MSTP polling to 3000mS, to ensure third party BACnet Devices that do not support COV subscriptions, are not overloaded.
Without this value set, it has occasionally been seen that Bacnet devices go offline or value readings stop updating the values.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 18404
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore