Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet binary value objects will pulse an Infinity output when they are used to set its value instead of turning it on.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet binary value objects will pulse an Infinity output when they are used to set its value instead of turning it on.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support
  • sesa116832
    sesa116832

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1567 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet binary value objects will pulse an Infinity output when they are used to set its value instead of turning it on.

Picard Product_Support
‎2018-09-06 02:53 PM

Issue

BACnet binary value objects will pulse an Infinity output when they are used to set its value instead of turning it on.

Environment

  • BACnet binary value object
  • Infinity output

Cause

People who are unfamiliar with programming for BACnet controllers may find it difficult to code their programs based on BACnet point values.

Resolution

When coding for Andover BACnet controllers, it is important to consider the differences between BACnet and Infinet point types. If you create a Numeric (configured as a binaryvalue) in a b3, b4 or BCX BACnet controller and you import that value into another controller for use in controlling an Infinity output, the output will pulse once on change of state (equivalent to output=1)and then shut off. Also, when changing the binaryvalue from inactive to active will cause the output to pulse as well.

When an Infinity output is set to Digital The default display format is $###. When the display format has been set to $### , values greater than zero will be displayed as ON, zero value will display as OFF and values less than zero will display as -ON if it is a tristate output. Changing this display format to ###.## will show the exact value of the output. On/Off or the analog value sent to it.

Use the blue BACnet folder and check that the source point is defined as a Binary Value and the Output is a Binary Output. If an Infinity Numeric was originally created as the default Analog Value and sent to database in the BACnet folders, it will have to be deleted and re-sent to database to get it into the correct Binary Value folder.

Example 1: The program below in the importing controller is a one-line looping program as follows:
output1= B4/B3/BinaryValue
A possible use for this would be a global occupancy point being used to turn the lights on.

Example 2:

  1. Write a PE program to copy a binaryvalue (BV) to a binaryoutput (BO).
  2. Set the BV to Inactive. Observe that the BO is Inactive.
  3. Set the BV to Active. Observe that the BO pulses for one second.

In order to import BACnet Binary values into another controller and use these points to drive an output on that controller you must use the BACnet point objects in your Plain English program as per below:
"Full BACnet Path" Binary Output Name = "Full BACnet Path" Binary Value Name

This will ensure that when the binary value is true, or "1", that the Binary output will go to "ON" and not pulse for 1 second.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2798
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore