BACnet alarm configured as Change of Value Event Type is not delivering an alarm when the alarm condition is met.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet alarm configured as Change of Value Event Type is not delivering an alarm when the alarm condition is met.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1872 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet alarm configured as Change of Value Event Type is not delivering an alarm when the alarm condition is met.

Picard Product_Support
‎2018-09-10 08:39 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM

Issue

Change of Value alarm is configured to alarm when an analog value changes by certain value but does not produce an alarm when the monitored object changes by that amount.

Environment

Continuum Cyberstation

bCX1

b3xxx

Cause

EventNotification or monitored object has not been configured properly.

Resolution

There are a number of configuration reasons for these Change of Value alarms to seem like they are not being delivered to the Workstation.

Check the Current State tab of the EventEnrollment to see if the ToNormal time is changing when you modify your monitored object. If this time is not updating then the EventNotification or monitored object are not configured properly, check the following:

  1. Confirm that the BACnet object type in the monitored object is configured properly. If this numeric is a number then it needs to be set to "AnalogValue".
  2. Confirm that a "send to database" has been performed on this controller on the BACnet side to send these points to the BACnet side. See details here on how to create BACnet alarms.

If this time is changing then the EventNotification and monitored object are configured properly but the alarm is not being delivered to your Workstation. Check  that one or more of the following is the cause:

  1. The Change of Value alarm will generate a ReturnToNormal alarm, confirm that the EventNotification is configured to Send Return to Normal alarms - this option needs to be ticked under "Send".
  2. Confirm that the option to  remove the alarm from the active alarm list is configured so that the alarm is not removed as soon as it is delivered. A selection of Returned to Normal or Acknowledged OR Returned to Normal on the Deactivate tab will mean that the alarm is removed from the active alarm list as soon as it is delivered. Select any of the following Deactivate options for the alarms to show up in the alarm list: Acknowledged, Acknowledged AND Returned to Normal, or Acknowledged AFTER Returned to Normal.
Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (1)
  • Find more articles tagged with:
  • 7251
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore