BACnet alarm Change Of State 'Alarm On' field is blank in the Algorithm page
  • BACnet alarm Change Of State 'Alarm On' field is blank in the Algorithm page
  • AbeMeran
    AbeMeran
‎2018-09-10 11:28 PM
BACnet alarm Change Of State 'Alarm On' field is blank in the Algorithm page.
Andover Continuum
  • CyberStation
  • bCX4040
  • b3s
BACnet alarm type must match the type of point that is associated with the alarm in the AlarmEnrollment object. For example, a Change Of State alarm requires a binary point.
Make the object BACnet object type match the alarm event type (Change of State, Change of Value, Out of Range etc).
In this example of a Change of State BACnet alarm, when the appropriate binary point is associated with the alarm, the 'Alarm On' field looks like this:
Tags (3)
  • 12359
  • alarm
  • algorithm
100% helpful (1/1)