Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

BACnet Programs Disable on a Reload

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet Programs Disable on a Reload
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Carl_Slack
    Carl_Slack
  • Clifton_eakes
    Clifton_eakes
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1686 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet Programs Disable on a Reload

Picard Product_Support
‎2018-09-06 02:28 PM

Issue

BACnet Programs Disable on a Reload

This is an issue that will be addressed, but in the meantime an explanation of how this happens and a workaround is provided below.

Environment

Infinity Program in a Continuum Bacnet controller

Cause

How this happens:

Create an Infinity Program in a Continuum Bacnet controller and then right click on the folder directory located under the controller you just created it under on the Infinity side. Now make sure there are two columns in the listview named State. You will most likely have to add one or both of these columns and make one of the columns source LIVE and the others source Database Notice when you run the listview both State columns will reflect Enabled for your running program.

Now, perform a find new bacnet devices if you haven't already and then perform a send to database on the controller you just created the Infinity Program under. At this point go back and either run or refresh your listview we ran earlier and notice the Infinity Programs State attribute is set to disabled in the database view.

At this point if you reload your controller in the Infinity side it will disable the program.

Resolution

Workaround on how to avoid this issue

After a newly created program has been sent to the database on the Bacnet side, immediately run the listview we created earlier and Highlight either all or only the programs that are set to disable for the State attribute where the source is set to Database. Once you have selected the rows of the programs you want to set to enable, select the Edit menu item in the listview. Now select set attributes.. and in the drop down select State for the name and enter Enabled for the value and select OK. This will allow the program's to be reloaded without being disabled. 

Most sites will never see this issue, since most will load up their controllers and back up the flash on the controller before performing a find new bacnet devices and send to DB on the bacnet side After controllers repower or reset the programs are just loaded back from flash. But the sites that reload their controllers will see the reload and programs disable issue. But like any reloading, you should always check your programs and alarms before leaving the site.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3883
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore