Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet/IP devices on different subnets are not discovered when doing a Discover on a Niagara G3 ENC controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet/IP devices on different subnets are not discovered when doing a Discover on a Niagara G3 ENC controller.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
6671 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet/IP devices on different subnets are not discovered when doing a Discover on a Niagara G3 ENC controller.

Picard Product_Support
‎2018-09-06 10:49 AM

Issue

There are BACnet/IP devices on several different IP subnets. Each subnet has one BACnet/IP device setup as a BBMD, however when doing a discover, no BACnet/IP devices from the different subnets are not being discovered.

Environment

Niagara G3, ENC-520

Cause

Setting up the BBMD in the ENC-520 is as simple as Changing its “Ip Device Property Type” from its default of “standard” to “Bbmd”. Once the ENC is configured as a BBMD device, then the BBMD’s required Broadcast Distribution Table (BDT) is automatically created. The ENC’s BDT includes its own IP address and Broadcast Distribution Mask (BDM), as well as the IP address and BDM of all other BBMD devices on the other IP subnets. The BDT allows for manual editing. We have found in some cases that the BDMs were being confused with the IP address subnet mask. The BDMs were being changed to reflect devices’ IP address subnet mask, which were something other that the standard BDM of 255.255.255.255. BBMD devices’ BDM must be set to 255.255.255.255.

Resolution

The Broadcast Distribution Mask must be set to “255.255.255.255” for each BACnet /IP Address listed in the ENC’s Broadcast Distribution Table. This is also true for other BACnet/IP devices configured as BBMDs on the other subnets.

1. Expand the ENC’s BACnetNetwork

2. Expand Bacnet Comm and then expand Network

3. Expand Ip Port and then expand Link

4. Expand the Broadcast Distribution Table

5. Expand any devices listed and set their Broadcast Distribution Mask to 255.255.255.255 for any one not listed as such. Save changes.

Try and discover again.
 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 12024
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore