Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

BACnet BDT on a BACnet BBMD becomes corrupted after upgrade

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet BDT on a BACnet BBMD becomes corrupted after upgrade
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • DavidFisher
    DavidFisher
  • DavidChild
    DavidChild
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2522 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet BDT on a BACnet BBMD becomes corrupted after upgrade

Picard Product_Support
‎2018-09-10 02:16 PM

Issue

BACnet Broadcast Device Table (BDT) on a BACnet Broadcast Management Device (BBMD) becomes corrupted after a server version upgrade, only if the BACnet BDT was taught from another BBMD

The following upgrades have this issue v1.5 to v1.6, v1.6 to v1.7, v1.7 to v1.8

Product Line

EcoStruxure Building Operation

Environment

  • BACnet Broadcast Device Table BBDT
  • BDT Management BBMD

Cause

  1. When a BDT is manually built (or BBMD first created), BDTE00001 is always set to the Server IP address. In the example this is 192.168.1.15
  2. When the BDT is taught from another BBMD, the BDT is changed and BDTE00001 is modified.
  3. When a Server (Enterprise or Automation) is upgraded (V1.5-1.6, 1.6-1.7, 1.7-1.8), then BDT entry BDTE00001 is changed to it's own IP address.
  4. Thus the Servers BBMD BDT can be corrupted with the Server IP address appearing twice in the BDT

Resolution

The taught BDT can either be set manually, before the upgrade, so it does not get corrupted by the upgrade process or be corrected following the upgrade.

Option 1: Change the BDT before the upgrade
The BDT Entry BDTE00001 should be set to the IP address the Server that contains it. The BDT Entry (BDTE00002 in the simple example above) that held the IP address of the Server should be set to the value that was in BDTE00001.

Option 2: Correct the BDT after the upgrade
For the first Server being upgraded

  1. Upgrade the Server
  2. Log into the Server and view the BDT from WorkStation
  3. Multi-select and delete all entries,
  4. Then manually reenter in all the BDT entries.

For all remaining servers being upgraded

  1. Upgrade the Server
  2. Log into the Server and view the BDT from WorkStation
  3. Multi-select and delete all entries
  4. From the First Server BBMD do a teach
  5. Verify the BDT table is in the Server

Below would be the first upgraded Server as option 2 or a corrected as option 1

 

NOTES

  1. Versions 1.8 and beyond include a fix so that the "BDT Teach" Mechanism does not allow the BDTE00001 to be changed.
  2. A hotfix will be available in V1.7
  3. Upgrading to a fixed version will not correct the issue, one of the two resolutions above will still need to be completed.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 18475
  • 30015
  • DavidShore20
  • defect
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore