Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Attempting to send email with I/A Series G3 and the SMTP server responds with an error "Must issue a STARTTLS command first."

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Attempting to send email with I/A Series G3 and the SMTP server responds with an error "Must issue a STARTTLS command first."
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1243 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Attempting to send email with I/A Series G3 and the SMTP server responds with an error "Must issue a STARTTLS command first."

Picard Product_Support
‎2018-09-06 12:25 PM

Issue

Attempting to send email with I/A Series G3 and the SMTP server responds with an error "Must issue a STARTTLS command first."

Environment

I/A Series G3

Cause

The targeted SMTP server requires an SSL / TLS encrypted connection.  SSL (Secure Sockets Layer) allows for the encryption of HTTP traffic between an ENC/ENS and a remote client. Encryption of the Fox and Platform protocol is not supported.  This implementation is supported with G3 versions 3.3 and above.  SSL can also be used to connect to a SSL enabled SMTP mail server to protect email credentials and the email message being transmitted.  Using SSL with SMTP is supported on version 3.4.55, 3.5.5, 3.6.31 or later.  As always it is recommended to use the latest maintenance build for each version of Niagara G3.

Resolution

The I/A Series G3 platform currently supports SSL encryption only.  Requires purchase of the crypto feature IA-SSL that adds the following line to the base license.

Contact Customer Care at 888-444-1311 to order (Part Number IA-SSL).  The Host ID for the ENC/ENS must be provided on the associated license form with the order.  The following feature will be added to the license.

crypto
ssl="true", parts="IA-SSL"

Install Updated License - Once the updated license is received, install the license into the ENC / ENS using Workbench.  Do not reboot when asked, you will reboot after updating the Crypto module.

Install Crypto module - Use the Software Manager in the Platform to install the crypto module.  Allow the ENC to reboot.

Install Crypto Service - Add Crypto Service to Services folder.

Configure Web Service (Only do this if you plan on using SSL with the Web Server).  Enable the Https Enabled property.  Change the Http Port to an unpublished port, such as 31876. This is required to prevent users from using HTTP logon.  Do not enable HTTPS Only.   This will cause the Fox Protocol not to function.

Configure Outgoing Mail Server (Only if SSL is required for email).  Configure as normal, except use SSL port for the port number and enable the Use Ssl property.  Contact your email provider for proper hostname and port number for SSL.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7807
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of