Attempt to commission b3 device fails with error 'Device other'
  • Attempt to commission b3 device fails with error 'Device other'
  • AbeMeran
    AbeMeran
‎2018-09-11 07:02 AM
AS trace log shows error 'Invalid device instance".
EXTRACT FROM TRACE LOG
2015-09-24 20:40:23.135 [1241912384] nsp.pin.BACnet Commission Canceled - Invalid device instance (AsyncCommands)
2015-09-24 20:40:23.142 [1241912384] nsp.pin.BACnet Command continuum.command.Commission failed. BACnet error 0x0 (AsyncCommands)
2015-09-24 20:40:23.144 [1241912384] nsp.pin.BACnet Command continuum.command.Commission failed: Device_Other (0xa0003) (AsyncCommands)
AS
BACnet
MSTP
The AS has detected a b3 device with the same serial number in the hardware folder.
Associate the device in the hardware folder with the device that you are trying to commission by dragging the device in the hardware folder and dropping it on the device under the BACnet interface that is being commissioned.
Note that the device's model numbers MUST be exactly the same in order for the association to succeed.
  • 18269