Application is giving excessive flow deadband when used with very slow VAV Floating Actuator.
  • Application is giving excessive flow deadband when used with very slow VAV Floating Actuator.
  • sesa116868
    sesa116868
‎2018-09-10 04:59 AM
MNL-V3 application configured with an external actuator of 390 seconds drive time shows an excessive setpoint deadband of almost 20% of control range.
MNL-V3 controller
Unknown - Issue has been reported to product management.
Here is an application fragment showing the issue.  Note the 390 second drive time.
Use the following application fragment in your application to eliminate the excessive >22%) deadband.
Here is an application fragment showing a suggested workaround:
  • TAC IA Series
  • 6742