Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Anti-passback (APB) and Access Initiated Control defined on the same door not working correctly

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Anti-passback (APB) and Access Initiated Control defined on the same door not working correctly
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Jeff
    Jeff
  • Tom_Poovey
    Tom_Poovey

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1421 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Anti-passback (APB) and Access Initiated Control defined on the same door not working correctly

Picard Product_Support
‎2018-09-07 01:17 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-25 10:19 AM

Issue

Anti-passback and AIC defined on the same door not working correctly

Product Line

TAC INET

Environment

I/NET Seven prior to rev 2.11

Cause

Before the release of I/NET Seven Rev 2.11 there was an issue with having APB and AIC on the same door. Basically the issue was the AIC function ran upon an entry into a zone, but it also ran the AIC function on the exit from the zone as well. This was an incorrect operation.

Resolution

In order to correct this function, a change was made in the AIC editor allowing the user to choose which reader (zone number) the AIC should run during a card read. Choose the entry reader (zone number) to have the AIC run only during an entry into that zone or choose the exit reader (zone number) to have the AIC run only during an exit from that zone.

Door editor settings

DoorEditor.png

 

On the right side of this window will be an entry zone of #3 and an exit zone of #1. This is a little confusing to people, in the Transaction table in AMT you will get a double transaction on an entry & exit card read.

For example during a card read with the settings above on an entry. You will get “Exit from Zone 1 and entry into Zone 3”. This is why the setting above is seen this way.

Zone lay out

EntryExit.png

 

As stated above the Transactions from an APB door will be this:

  1. Entry read—Exiting from Zone 1 and entering Zone 3
  2. Exit read --- Exiting from Zone 3 and entering Zone 1

AIC Settings

AIC.png

 

In the AIC setting above the Zone listed is #1, in the case the AIC will run only during an entry card read based on the setting in the Door editor above.

Now if you want the AIC to function only on the exit from Zone #3 then replace the #1 in the APB zone above with in this example #3. In this case the entry reader will only let you in the door (NO AIC functions) and upon the exit from Zone 3 the reader will open the door and also give the AIC functions.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 2495
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore