Issue
Analog Producer value located in an RP-C controller cannot command light object(BACnet type: crs-lighting-output) or blind object(BACnet type: crs-blind-output) located in another RP-C's CRS expansion module.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Room Controller (RPC) 24 V
- Building Operation Room Controller (RPC) 230 V
Cause
Light and Blind objects support only two priorities (1 - Force, 2 - Normal). An error will be returned by the RP if the Priority in the Write request from the Producer Value is outside this range, ex. Priority 16.
Resolution
In the Analog Producer Value, set the default priority for writing to 2 (normal) or 1 (Force), as shown in below screenshot: