An unexpected error occurred while downloading using a Xenta Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • An unexpected error occurred while downloading using a Xenta Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4159 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

An unexpected error occurred while downloading using a Xenta Server

Picard Product_Support
‎2018-09-10 01:00 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:01 AM

Issue

"An unexpected error occurred" shown while downloading a LonWorks device through a Xenta Server

Product Line

TAC Vista

Environment

  • TAC Xenta Server (511, 527, 555, 701, 711, 721, 731, 913)
  • TAC XBuilder
  • TAC Vista Server

Cause

There are a couple of reasons that you can get this error message.

One is that SSL 3.0 is not enabled in Internet Options for the Windows user running TAC Vista Server. This will keep Vista Server from being able to download a Xenta controller using a Xenta Server.  It will also not let you download and XBuilder project to the Xenta Server, and you can not connect to the browser of the Xenta Server using Internet Explorer.

The other reason could be, that while running Vista Server as a service, the Windows account running the service is Local System and that this account does not have SSL 3.0 enabled.

This could also occur if you have enabled "System cryptology: Use FIPS compliant algorithms for encrypting, hashing and signing" in the local policy setting.

Resolution

Enabling SSL 3.0

  1. Go to Control Panel and open Internet Options.
  2. Choose the Advanced tab and scroll to the bottom of the Settings list.
  3. Near the bottom you will see Use SSL 3.0.  Make sure the Use SSL 3.0 box is checked.

Configuring the Windows account running TAC Vista Server

  1. Download the TAC Vista Run Mode tool and run it.
  2. Under the Service Logon section choose Local User for the Logon Type, select or write the Windows user name and password.
    • It has to be the account you are currently logged in with, or another user having enabled SSL 3.0 and has administration rights.
  3. Restart the service.

 

Check the local security policy for FIPS

  1. Open Control Panel - Administrative Tools -Local Security Policy (or type secpol.msc in Start-->run)
  2. Go to Local Policies-Security Options
  3. Find System cryptology: Use FIPS compliant algorithms for encrypting, hashing and signing
  4. Change to disable, apply-OK
  5. Restart XBuilder
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 18930
  • unable
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore