An override command was applied to a Network 8000/DMS standard point on a SIGNAL graphic. The graphic now shows the point is in override but the actual point in field panel is not ...
  • An override command was applied to a Network 8000/DMS standard point on a SIGNAL graphic. The graphic now shows the point is ...
  • sesa119747
    sesa119747
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 02:49 PM
An override command was applied to a Network 8000/DMS standard point on a SIGNAL graphic. The graphic now shows the point is in override but the actual point in field panel is not in override.
  • Network 8000
  • SIGNAL
When override commands in SIGNAL do not apply properly, the actual point in field panel will not be in override.
it is best to clear the data file and try applying them again. Follow these steps:
  1. Shutdown SIGNAL and open up Windows Explorer.
  2. Find the override.dat file in the C:\Windows\Override directory and delete it.
  3. Re-start SIGNAL.
  4. Apply override commands again. (The override.dat file will be re-created)
  • TAC IA Series