Although the current time is correctly displayed in a UNC, the Enterprise Server, and WorkPlace Pro, it is incorrect in the R2 Schedule Editor.
  • Although the current time is correctly displayed in a UNC, the Enterprise Server, and WorkPlace Pro, it is incorrect in the R...
  • SESA113595
    SESA113595
‎2018-09-07 09:03 AM
Although the current time is correctly displayed in a UNC, the Enterprise Server, and WorkPlace Pro, it is incorrect in the R2 Schedule Editor. The error in time is a multiple of one hour.
I/A Series R2 (Niagara), all versions.
The correct Time Zone is not synchronized in the Schedule Editor, which defaults to timezone=America/New_York.
1. Close WPPro
2. in Windows, go to Niagara / build / nre / lib /time.properties, open with a text editor
3. If it reads timezone=America/New_York, change it to timezone= (timezone corresponding to your location. Copy from Niagara / build / nre / lib /timezones.txt)
4. Save the change
5. Start WPPro, check the time in the Schedule Editor, should be correct.
  • TAC IA Series
  • 14024