Issue
Alarm message received "Trend Log Object [Object Name]. Could not transfer log values automatically. Try Manually"
Environment
- Vista Server
- Xenta Controllers
Cause
- Log space set to 0 seconds or minutes for trend log.
- Communication breakdown between Vista and Xenta Controllers.
Resolution
- Set Log Space to minimum 10 sec or 1 min per trend log
- Communication between Xenta and Vista should be normal.