Issue
Generating a Menta application results in the following error if the maximum number of Menta blocks is exceeded in the application:
TAM32
The maximum number of Alarm blocks is exceeded in the application.
The problem must be solved before the application can be generated.
Product Line
TAC Vista
Environment
- Menta
- Xenta programmable controllers
- Xenta 281, 282, 283, 301, 302, 401, 401:B
Cause
Generating a Menta application results in an error if the maximum number of Menta blocks is exceeded in the application.
Resolution
There can be no more than 127 alarm blocks in a Menta application.