Airflow reading in Xenta 102-AX fluctuates or is zero

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Airflow reading in Xenta 102-AX fluctuates or is zero
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1418 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Airflow reading in Xenta 102-AX fluctuates or is zero

Picard Product_Support
‎2018-09-06 01:10 PM

Issue

Airflow reading from Xenta 102-AX is jumping around and will not stabilize or is 0.

Environment

  • Vista
  • Xenta 102-AX Plug-in
  • LonMaker, NL-220

Cause

For a variety reasons parameters may get changed in a Xenta 102-AX adversely affecting the controller's performance.

Resolution

Ensure that all of the parameters that affect the airflow reading are set properly. In some cases it may be best to restore the default parameters.

Parameters that should be checked may be found through the Xenta 102-AX plug-in or through Vista but are grouped below how they are found in the plug-in starting with Unit Parameters:

Unit Parameters

Duct Area

Ensure that the duct area is set properly for the box size. If a formula was used to determine the duct area from duct diameter verify that it yielded the correct result.

For square or rectangular ducts use the following formula:

For round ducts use the following formula:

Pickup Factor

The pickup factor is sometimes known as the K factor and is determined by examining the airflow curve diagram provided by the box manufacturer. It can often times be found on the box itself or in the manufacturer's literature. If the manufacturer's specs cannot be obtained use the default pickup factor, which is 2951.6.

Box Constant

The box constant is a product of the pickup factor and the duct area. It is sometimes available from the box manufacturer. If the manufacturer's data cannot be obtained use the default value, which is 1588.5.

Note that the box constant will be changed from default if a CBC, or, calibrate box constant is performed.

Airflow Parameters

Velocity Pressure Gain

The default settings here are 10 / 10 and are changed when a calibration is performed. If these numbers factor out to be very far from one you may want to reset them to their defaults and investigate if something went wrong with the calibration. For example these values may read 2957 / 3054 but since that factors out to 0.968 which is only about 3% off from one. However, if these numbers were 2957 / 6043 this would be a clear indicator that there was something wrong.

Velocity Pressure Offset

The default value here should be zero and considering that sensor is nominally set up for a 0-1" scale numbers greater than +0.1 or less than -0.1 should be cause to investigate further for mistakes during the calibration process.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6537
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of