After updating bin file to an SCU, Deny Entry Tenant message in AMT or access denied.
  • After updating bin file to an SCU, Deny Entry Tenant message in AMT or access denied.
  • sesa139513
    sesa139513
‎2018-09-06 02:25 PM
Problem with downloading bin file with more than one door defined causes second set of doors to deny reads.
Bin files connected to this issue are 3.24, 3.25, 3.26
TAC I/Net Seven using Access Control. SCU 1284 configured with two doors. (Dip Switch 6 ON gives double address)
Bin file failure to download with double address setting.
On an SCU, an SCU is configured for 4 doors. 2 of those doors are working. 2 of the doors on the SCU are not working.
Only thing that has changed is the SCU was downloaded with a new bin file. Nothing in door configuration was changed, no dip switches were altered.
Solution:
Find out which doors were not working, (probably the second two doors like 0104)
Go to Edit/controller/MCU Configuration and Set those doors to Internal, and then download the SCU with the bin file again.
Go to Edit/controller/MCU Configuration and Set the doors back to DPU.
  • TAC INET
  • 4003