Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

After replacing an MNL controller, WorkPlace Tech reports an error indicating that the application requires a different controller type.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • After replacing an MNL controller, WorkPlace Tech reports an error indicating that the application requires a different contr...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1584 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

After replacing an MNL controller, WorkPlace Tech reports an error indicating that the application requires a different controller type.

Picard Product_Support
‎2018-09-06 01:25 PM

Issue

After replacing an older revision MNL controller with a new one, WorkPlace Tech is unable to download the existing application file into the new controller reporting an error "The selected device is Invensys IA(x) ... controller, the application requires Invensys IA(y) ... controller".  In this error message the controller type info (...) will be the same in both parts of the message but the IA(x) and IA(y) part of the message is different. 

Environment

MNL-50
MNL-100
MNL-110,
MNL-130,
MNL-150,
MNL-200,
MNL-Vx

Cause

Replacement controller is of the same type but of a different version.

This issue occurs any time a version 2 controller is replaced with a version 3 controller.
for example, this error will occur if a MNL-V2RV2 controller is replaced by the newer version, MNL-V2RV3.
 

Resolution

  1. Open application in the WorkPlace Tech Tool.
  2. Open the Hardware Wizard and click the [Back] button to open the Controller Selection page.
  3. When the Controller Selection page has been opened, you will note that the [Older] tab has been displayed with the existing controller type displayed.
  4. Select the tab corresponding to the controller type, for example if replacing a MNL-V2RV2 controller, select the MNL-VAV tab.
  5. Select the model of the replacement controller, for example when replacing a MNL-V2RV2, the replacement is the MN-V2 [MNL-V2RV3].
  6. Click the [Next] button to complete the selection of the replacement controller type then click the [Finish] button to close the Hardware Wizard.
  7. Recompile the application and download it to the replacement controller.

If the controller is part of a LON network that has been commissioned by a LON Network Management tool, it will be necessary to replace the existing device object and commission the new controller.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5942
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.