After installing Continuum, intermittent Communication issues on BACnet and Infinet BCX controllers
  • After installing Continuum, intermittent Communication issues on BACnet and Infinet BCX controllers
  • sesa116832
    sesa116832
‎2018-09-06 01:53 PM
After installing Continuum, intermittent Communication issues on BACnet and Infinet BCX controllers, graphics are not updating, and points may or may not be edited. Each of 3 workstations are exhibiting similar issues, but not with the same controllers. Workstation 1 may be able to edit points in BCX1, but not BCX2.  Workstation 2 may edit points in BCX2 but not BCX1.
LAN with SQL Server 2008, all workstations with XP service pack 3.
The workstations were initialized with Node ID's that were conflicting with the BCX node ID's.
With one workstation logged into Cyberstation, the workstation objects were exported from a workstation that was logged out of Cyberstation. Once all required exports were completed, that workstation was deleted from the object tree.
That workstation was then initialized with ID's that would not conflict with the BCX ID's.
Cyberstation was then started on the newly re-configured workstation and graphics were tested, and points were edited without issue.