Issue
After upgrading the Continuum workstation software, cannot edit workstation programs
Environment
Continuum Cyberstation
Workstation programs
Plain English
Cause
Not able to edit workstation programs. Firing order is edit locked.
Resolution
To resolve open up the Continuum Commandline program and type in "Firingorder editlock=false"
This will unlock the firing order and programs will be able to be edited.
In the simple case of editlock where a program may have been editlocked which is different than firing order editlocked. Simply select the program in question and press Ctrl+U or access the properties of the program by right click and select the CurrentStatus tab and press the "Force Object to unlock" button.