Advanced Display is loosing connectivity if AS-P is power cycled (or USB disconnected)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Advanced Display is loosing connectivity if AS-P is power cycled (or USB disconnected)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1665 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Advanced Display is loosing connectivity if AS-P is power cycled (or USB disconnected)

Admiral David_Kendrick Admiral
‎2019-11-04 08:06 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:32 AM

Issue

Advanced Display Version 2.0 Tablets are loosing connectivity to their associated AS-P (connected via USB) when the AS-P is power cycled or the USB is briefly disconnected, even after the connection/power has been restored.

Product Line

EcoStruxure Building Operation

Environment

Advanced Display V2

Cause

There are a number of internet browsers available to the user of an AD V2 once the SmartX Kiosk App has been entered.

Chrome has been included in the standard view of the Kiosk for some time.

chrome.png

and using the 'show/hide system apps' button within the Kiosk the other apps can be accessed on the tablet such as Samsung's own Samsung Internet App (as long as as the Kiosk pin is used).

samsung.png

However since the release of Kiosk 8.1 only the Webstation App, which is built into the Kiosk is supported for connection to the AS-P and to use Kiosk 8.1 or greater the Android 8.0 build firmware of the AD V2 must also be brought up to T580XXU4CSA1 as a minimum.  (as detailed by TPA-EBO-19-0002.00)

Using the Chrome or Samsung internet apps or having an older build of Android 8 OS firmware may appear to work fine on first impressions, but connectivity issues may then arise such as those detailed above

Resolution

As long as AD V2 build is T580XXU4CSA1 or greater and the inbuilt Webstation App is being used for all AS-P connection, then users should not encounter any connectivity dropout at all and any new issues which arise can be raised with Product Support Services.

build.png

webstation.png

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidKendrick19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore